coulter said:
3. The concern is will the conductors carry the required current with out exceeding their temp rating. This is not a house panel with a 75C rating. Hopefully your engineer paid attention to the specific equipment temp specs.
Carl,
I appreciate your explanation of the field supply current vs. voltage! You make it easy to understand.
Now to answer a few of your questions:
1) The generator was put into service in 1967
2) It is a 43,125 KVA unit propelled by water
3) I?m doing the electrical circuitry related to the unit that is currently being rewound. My portion is design build in that we?ll upgrade chosen circuitry while the unit is down.
The DLO cable we purchased is actually rated as RHW-2
I understand the NEC ?is not intended as a design specification or an instruction manual? (90-1(B)) - so it
is not a design guide -
BUT it certainly qualifies installations to meet the purposes listed in 90-1(A)(B)
My greatest concern is common with yours in that I want to supply adequate conductors to meet the overcurrent protection. Even though NEC does not apply in a powerhouse the fact remains I have 600A overcurrent protection for circuitry in conduit, so the question is
what size conductors are required? And I come up with quad 313 mcm?s. I?ll admit I do get stuck around NEC as it is proven.
Thanks for your input!