Announcement

Collapse
No announcement yet.

Continuous GEC from Ground Rod to Water

Collapse
This topic is closed.
X
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

    Continuous GEC from Ground Rod to Water

    On a new 200amp service, Does the grounding electrode conductor have to be unspliced from the panel to the ground rod and to the water pipe within 5' of the water entrance to the house? Every section I read says it only needs to be unspliced to the most convieniant electrode, then bonding jumpers to all of the other electrodes. If the water line is 100' away, can't I just go to the driven ground rod 1st and then add another clamp to the water line? Everyone in my office says this has to be continous through all electrodes with no splices except for welding or irreversible clamps. Thanks Everyone!!

    #2
    You are correct, see this on going thread.

    Roger
    Moderator

    Comment


      #3
      The GEC can end at the first electrode. From there you may join other electrodes with bonding jumpers. If you had a building with building steel bonded at the service and a water pipe 300' away you could just bond the water pipe to the building steel with a bonding jumper. The GEC is the conductor between the neutral and the electrode itself it does not need to continue unbroken to any other electrodes.
      Rob

      Moderator

      All responses based on the 2017 NEC unless otherwise noted

      Comment


        #4
        If your water pipe is 300 feet away, chances are pretty good that its not inside the building we are talking about here, in which case the 5' rule doesn't apply either . 250.52
        85deg. an Sunny today.

        Comment


          #5
          Thanks for all of the info!! you guys are the best!! ::grin:

          Comment


            #6
            Originally posted by macmikeman View Post
            in which case the 5' rule doesn't apply either . 250.52
            I don't understand why not ?
            Frank Arizona,USA

            Comment


              #7
              Originally posted by benaround View Post
              I don't understand why not ?
              Did you read the code reference I gave? I'll elaborate, first word of the second sentance of 250.52. It is almost universal in overlooked when this code is read.
              85deg. an Sunny today.

              Comment

              Working...
              X