HPS Fixtures

Status
Not open for further replies.

svaurez

Member
Location
California
I was taking voltage readings at the socket of a high pressure sodium fixture and it read 153 volts.I checked another one and it was 160.Is this normal for this type of fixture?The line voltage is 120.
 

-marty

Senior Member
Location
Alaska
Re: HPS Fixtures

The voltages both sound within range. I had a problem with a hps and my supplier gave me an 800 number for Lithona's tech support.
 
Re: HPS Fixtures

do you know what wattage it is ?? if 35 to 150 watt typically run little over 120 volts but note that 150 watts do come in 2 diffrent version is 55 volts or 100 volts rating it can make a diffrence with it for 150/100 to 400 watts hps typacally near 200 to 240 volts range i am not sure excat numbers but what ballast it can make a big diffrence with it but i will post the listing later with corret voltage ( i have a chart with me in my shop i will pick it up later)

merci marc
 
Status
Not open for further replies.
Top