it's been a while since ive de-rated for conduit fill so my question is, how many 3 hot/1 neutral groups can i put in a 3/4'' pipe if the wire is #12 thhn, and on a 20 amp ckt and the terminal ratings are unknown. i am confused if it is 30a X 70%=21a or if i have to base it off of the 75 degree column. anyway i would like to put 9 #12 hots with 3 neutrals in a 3/4'' on a 20 amp ckt.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
First you need to determine if the neutrals are considered current carrying conductors based on 310.15(B)(4). If they're not your 9 circuits will have 9 CCC's. Next you'll need to determine the ampacity of the conductors based on their insulation and derate from there.
 