A client has an old Federal Pacific Substation: 4160 V primary, 208V secondary, 225 KVA.
The substation has an integral distribution panel (Federal Pacific again) with a 600 Amp main, and about 8 breakers.
The client would like to add more load to this substation, but the problem is the distribution panel is already full of 100 amp and 150A amp breakers.
Normally, I'd install a larger breaker and move some of the smaller feeds to a sub-distribution panel. But since its Federal Pacific, I can't get any new breakers for this substation.
Is it legal to tap the bus (load side of the main breaker) and run a feed to a new distribution panel? I can set a fused disconnect if necessary to comply with the tap rules, but I'm actually thinking about running full sized wire (600A) wire to the new panel.
This substation is in a school's corridor, so I want to make sure whatever I spec. is allowed.
Steve
The substation has an integral distribution panel (Federal Pacific again) with a 600 Amp main, and about 8 breakers.
The client would like to add more load to this substation, but the problem is the distribution panel is already full of 100 amp and 150A amp breakers.
Normally, I'd install a larger breaker and move some of the smaller feeds to a sub-distribution panel. But since its Federal Pacific, I can't get any new breakers for this substation.
Is it legal to tap the bus (load side of the main breaker) and run a feed to a new distribution panel? I can set a fused disconnect if necessary to comply with the tap rules, but I'm actually thinking about running full sized wire (600A) wire to the new panel.
This substation is in a school's corridor, so I want to make sure whatever I spec. is allowed.
Steve