Raceway for walk-in freezer.

Status
Not open for further replies.
What raceways are permitted in a walk-in freezer for lighting circuits? The installers have the switches mounted in the freezer wall and left bell boxes for connecting the switch legs to the lights. I wanted to use nonmetallic flexible conduit but am concerned about temperature rating and physical damage.
 

MarkyMarkNC

Senior Member
Location
Raleigh NC
I usually use EMT with compression fittings. If it is a restaurant, the health inspector is probably not going to allow flex inside a walk-in cooler.
 
Last edited:

hurk27

Senior Member
Depending upon where the conduit will be located, I will run EMT with WP seal connectors in areas not subject to racks hitting it, but in rack areas I will run RMC, unless some kind of protection can be provided.

The last one I did, all the wiring was done outside of the freezer and the light box was a sealed type box the freezer company supplied that was mounted into the ceiling with the back accessible from the top. light switches was outside.
 