    Load calcs for electric Ranges - 220.55

    This section says "Where two or more single-phase ranges are supplied by a 3-phase, 4-wire feeder or service, the total load shall be calculated on the basis of twice the maximum number connected between any two phases"

    I am not quite sure what it means by twice the maximum number connected between any two phases Can someone explain this to me?

    I looked up the example D5(a) i Annex D. The example has 10 ranges in 20 dwelling units, 120/208V, 3ph 4w system...It says "the maximum number between any two phase legs = 4" How do they get 4?

    Thanks.

    #2
    Originally posted by elec_eng View Post
    I looked up the example D5(a) i Annex D. The example has 10 ranges in 20 dwelling units, 120/208V, 3ph 4w system...It says "the maximum number between any two phase legs = 4" How do they get 4?
    In the Annex D example with 10 ranges on a 120/208V, 3ph 4w system, they figure that if the ranges were balanced as best as possible, you'd have 4 units on A-B, 3 units on B-C and 3 units on C-A. So 4 is the maximum number connected between any two phases.

    Comment


      #3
      Got it...Thanks.