CB or conductor termination contact resistance

Status
Not open for further replies.

ron

Senior Member
Does anyone know a reference that may show generally acceptable resistance for circuit breaker contacts, switch contacts and conductor terminations?

I was guessing at 100 micro-ohms for 4000A LVPCBs but wasn't sure for long barrel compression and mechanical set screw type conductor terminations.
 

zog

Senior Member
Location
Charlotte, NC
Does anyone know a reference that may show generally acceptable resistance for circuit breaker contacts, switch contacts and conductor terminations?

I was guessing at 100 micro-ohms for 4000A LVPCBs but wasn't sure for long barrel compression and mechanical set screw type conductor terminations.

Depends on the exact breaker but for a 4000A LVPCB you should see <20 microhms.
 

ron

Senior Member
The reason for the question is due to an underrated piece of switchboard.
It is existing and installed about 5 years ago.
The three phase bolted fault calculated result is below the SWBD AIC/withstand rating. The x/r ratio at the board is >6.6, so with the derating, the board and its cb's are now underrated.
Since the IEEE/ANSI method of calculating fault current is conservative, and ignores small impedances such as contact resistance, I thought if I added them into the model, it would calculate a value below the rating.
Also due to the high x/r value, the L-G calculation is higher than the three phase bolted fault value, so I'm just trying to add real life impedance to ensure the equipment is adequately braced.
 