hvac nameplate
In an HVAC unit with multiple compressors, fans, etc, are the fla, lra, and rla amperage ratings on the data plate cumulative or per?
Thank you.
infinity
New Jersey
Journeyman Electrician
Thank you.
Do you need to know more than the MCA and the Maximum Overcurrent Protection Device size?
Welcome to the forum. :)
bob
Alabama
You should find the MCA and the Maximum Overcurrent Protection Device size
on the name plate for the unit.
LarryFine
Henrico County, VA
Electrical Contractor
I would think that a single nameplate on the unit refers to the unit as a whole.
(I'd be very grateful to the manufacturer for sticking one on. ;))
And, ditto on the welcome! :)