I'd like to confirm the conductor size required by NEC for a power cord on a small pump. When I determine the voltage drop for the below values, I find 2.1 volts (1.75%). This would tell me the 16/3 cord should be adequate, as long as it has the ampacity (and it should). Yet many online calculators I've used recommend 14 gage wire, even if I reduce the cord length to 5 feet. Is there an NEC requirement that drives this? Thanks.
Full load current = 4.2 amps
Cord length (pump to plug) = 50 ft
Conductor size = 16 AWG, 3C (copper)
Supply voltage = 120 VAC
Full load current = 4.2 amps
Cord length (pump to plug) = 50 ft
Conductor size = 16 AWG, 3C (copper)
Supply voltage = 120 VAC