Strahan
Senior Member
- Location
- Watsontown, PA
I have recently run into a problem that I'm having trouble explaining to my men. We have a 3HP Allen Bradley 160 variable frequency drive controlling a 1.5HP motor rated at 2.4amps. The drive rated output current is 6A continuous. The problem lies in my current readings. If I use the HIM on the drive to display output current it reads 3.0 - 3.2A and when I put my Fluke 322 clampmeter on each leg it reads 2.4-2.8A? Each leg reads the same with my meter. Why the big difference?
I have noticed this throughout our plant with all our 160 AB drives. Now I have also compared these drives to our powerflex 40's and they display very close to my meter readings. Is it something just with these drives?
Next question would be how to set my trip current setting? Service factor of motor is 1.15 so I can size at a max of 125%. 2.4 * 125% = 3A. Well of course the drive trips. What reading do I use? Now I do presume a mechanical issue with this machine because either way the motor is running more loaded than it should, but this circumstance has brought this problem to my attention. According to the clamp I'm still good on current draw, but according to the drive I am not
I have noticed this throughout our plant with all our 160 AB drives. Now I have also compared these drives to our powerflex 40's and they display very close to my meter readings. Is it something just with these drives?
Next question would be how to set my trip current setting? Service factor of motor is 1.15 so I can size at a max of 125%. 2.4 * 125% = 3A. Well of course the drive trips. What reading do I use? Now I do presume a mechanical issue with this machine because either way the motor is running more loaded than it should, but this circumstance has brought this problem to my attention. According to the clamp I'm still good on current draw, but according to the drive I am not