Hi, Sorry, new engineer here.
I think I know how NEC instructs to size motor feeders and disconnects; I have a 3phase, 10HP @ 208V.
1. So per table 430-250, the cable has to be 30.8 X 1.25 (about 40A).
2. motor Overload should be name plate FLC X 1.25 (about28A).
3. and per table 430-52, short circuit/GF breaker is 2.5 X name plate FLC (about 60A).
What if the overload is located near the load (not immediately after the breaker)? Can I still size the breaker higher than cable rating?
Thanks
I think I know how NEC instructs to size motor feeders and disconnects; I have a 3phase, 10HP @ 208V.
1. So per table 430-250, the cable has to be 30.8 X 1.25 (about 40A).
2. motor Overload should be name plate FLC X 1.25 (about28A).
3. and per table 430-52, short circuit/GF breaker is 2.5 X name plate FLC (about 60A).
What if the overload is located near the load (not immediately after the breaker)? Can I still size the breaker higher than cable rating?
Thanks