    Lightning Protection

    If you have a lightning protection system with a ground loop, I know you are required to have a downcomer every 100ft. But my question is since you have the loop, does the downcomer still have to terminate in a ground rod?

    Thanks

    #2
    Originally posted by ampal View Post
    But my question is since you have the loop, does the downcomer still have to terminate in a ground rod?
    No there is no requirement to do that. However from a design POV you do not want to connect the down conductors to the ring. You want to drive a rod and connect to the down conductor.

    The only place want to bond the two together is at the service entrance.

    Comment


      #3
      Originally posted by dereckbc View Post
      No there is no requirement to do that. However from a design POV you do not want to connect the down conductors to the ring. You want to drive a rod and connect to the down conductor.

      The only place want to bond the two together is at the service entrance.
      What about exhibit 250.31?
      Inspector MikeĀ®
      ESI

      Comment


        #4
        I see, thanks guys, it seems that the ground ring and well are connected indirectly, I've seen some designs where the downcomer crosses the ring and terminates in a ground well..