Instantaneous circuit breaker as disconnecting means

Status
Not open for further replies.

philly

Senior Member
Would an instantaneous circuit breaker in a listed combination starter be considered a motor disconnecting means and thus apply to 430.110 which states that the ampere rating of the disconnecing means must be at minimum of 115% of motor FLA? Would this therefore mandate that the instantaneous breaker must have an ampere rating of at least 115% of motor FLA with adjustable settings up to that allowed by 430.52?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Would an instantaneous circuit breaker in a listed combination starter be considered a motor disconnecting means and thus apply to 430.110 which states that the ampere rating of the disconnecing means must be at minimum of 115% of motor FLA? Would this therefore mandate that the instantaneous breaker must have an ampere rating of at least 115% of motor FLA with adjustable settings up to that allowed by 430.52?
Yes, in a "listed combination starter" the breaker will be properly sized as such by the manufacturer for the maximum HP as stated on the combo starter nameplate.
 