I have a control panel with 3 480V 1 HP starters. I want to oversize the main disconnect circuit breaker for the panel so that I can add more starters in the future. Is there a limit as to how large the breaker can be?
Depends. First, are they individual motor loads or combination motor loads?I have a control panel with 3 480V 1 HP starters. I want to oversize the main disconnect circuit breaker for the panel so that I can add more starters in the future. Is there a limit as to how large the breaker can be?
Thank you for your replies. Yes, this is an industrial control panel and the 3motors (FLA 2.1A) have their own starter, overload, and fuses (4A).
I did a little searching and saw this post here so I'm thinking that the OCPD could be sized larger as long as the feeder is size larger as well?
Yes it's an industrial control panel and the motors have individual fuses and overload for protection. From this post, it appears it's ok to oversize the OCPD.
As I mentioned in post #3, "See 430.53 then (A) and (D) thereto..." 430.53(D) covers "Single Motor Taps", while (A), (B), or (C) covers the permitted OCPD of the "feeder"... which is called a branch-circuit in that section (don't ask me why, 'cause I don't know). 430.53 requirements must be met in addition to those of Article 409.Generally, I would agree with you. It is common practice to tap disconnects, panels, etc. from a larger feeder, however, unless I am mis-reading (highly possible), it appears that in a Art 409 situation, unless the panel has a single main overcurrent protective device, you can not size the feeder OCP larger than specified in 409.21(c).
It seems this falls in line with the 240.21 tap rules which often require
singular OCP at the end of the tap.