flexible conductor rating & fill

Status
Not open for further replies.
Can anyone help me with allowable ampacities and conductor fill for extra flexible copper conductors? I've found the following: COBRA WIRE & CABLE X-FLEX? E NUMBER (UL) BC5W2 OR MTW OR THW FT4 OR AWM 1232/1284/1338/10070 600V OR 10269 1000V VW-1 SR AWG SIZE LL NUMBER CSA TEW 105?C 600V OR AWM I A/B 105?C 600V O FT1 ROHS COMPLIANT MADE IN USA.
Q. Where can I find, or how can I determine, conduit fill requirements for this type cable installed in EMT. This is for a 75kw (55hp) motor that has been pre-fitted for a European type cable installation. We plan to use seal tight with extra flexible conductors for motor terminations. Thanks!
 
rating & fill

rating & fill

Thanks guys. We used table 4 to determine the allowable conduit space as well as solving for total conductor space by multiplying conductor radius squared by pi and adding together.
 