    flexible conductor rating & fill


    #2
    I would either measure the cable or call the manufacturer and find out what the cir. mil. is of the cable.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky

    Comment


      #3
      http://www.cobrawire.com/x-flex/x-flex.php

      If you scrool down the nominal OD is listed for the various sizes.
      Why is it, when it comes to the NEC, the obvious is never simple and the simple is never obvious?

      Comment


        #4
        rating & fill

        Thanks guys. We used table 4 to determine the allowable conduit space as well as solving for total conductor space by multiplying conductor radius squared by pi and adding together.

        Comment


          #5
          Originally posted by cmonin View Post
          We plan to use seal tight with extra flexible conductors for motor terminations.
          Is that compliant?


          400.8 Uses Not Permitted.
          (6) Where installed in raceways, except as otherwise permitted in this Code

          Comment