    Originally posted by cmonin View Post
    We plan to use seal tight with extra flexible conductors for motor terminations.
    Is that compliant?


    400.8 Uses Not Permitted.
    (6) Where installed in raceways, except as otherwise permitted in this Code

    Leave a comment:


  • cmonin
    replied
    rating & fill

    Thanks guys. We used table 4 to determine the allowable conduit space as well as solving for total conductor space by multiplying conductor radius squared by pi and adding together.

    Leave a comment:


  • billsnuff
    replied
    http://www.cobrawire.com/x-flex/x-flex.php

    If you scrool down the nominal OD is listed for the various sizes.

    Leave a comment:


  • Dennis Alwon
    replied
    I would either measure the cable or call the manufacturer and find out what the cir. mil. is of the cable.