This is incase the primary is a 480/277
If you either bond the primary XO to an EGC or feed it with a supply neutral on a common core transformer and the secondary has line to neutral loads that become unbalanced (most likely will) this will cause high heating in the transformer cores and place high currents on this bond conductor, I have seen them burn off before, always feed a common core transformer line to line only and don't bond the primary XO
Otherwise Don is correct, supplying a primary neutral to the secondary XO will result in a rebonding of the grounded conductor which is not allowed in the NEC after the main bonding jumper in the service. but the secondary does have to have the XO grounded, this allows a fault current path in the event of a ungrounded circuit from this transformer coming into contact with any metal surfaces that is grounded to the supply side.