raider1

Senior Member
Staff member
Location
Logan, Utah
Friends, would NEC 450.5 (A) (2) be the correct article to apply to calc OCP for 30kva dry transformer?

Most likely not unless you are using one of the configurations mentioned in 450.5.

450.5 is for autotransformers, which have a common winding.

For a standard dry type transformer look at 450.3 for your overcurrent protection requirements.

Chris
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I agree with Raider. But don't forget you also have to protect the conductors. So 240.21 will also come into play.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I agree with Raider. But don't forget you also have to protect the conductors. So 240.21 will also come into play.

Good point, a lot of times the fact that 450.3 only deals with overcurrent protection of the tranformer itself is overlooked.

Chris
 