220.40 vs. 220.84

Status
Not open for further replies.

olc

Senior Member
The optional load calculation for multifamily almost always comes out significantly less than the standard calculation. I feel like I am missing something. Are we comfortable with the optional 220.84 calculation?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
The optional load calculation for multifamily almost always comes out significantly less than the standard calculation. I feel like I am missing something. Are we comfortable with the optional 220.84 calculation?

Yep, either method is acceptable.

It is typical that the optional method will give you a smaller service size than the standard method.

Chris
 
Status
Not open for further replies.
Top