Apartment grounding question.

Status
Not open for further replies.

kbrandt

Member
Location
arizona
I have 2 apartments that need service upgrades. 100 amp each.

Each has its own meter for gas and water, we have to bond gas and water to the ground rod, here.

I know I can use 1 ground rod, but do I have to bond both gas and water for each apartment or just hit one? And were in the code book does it address this question.

The service wires tie in both from one drop.

Thanks for any input.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I would say it would depend on if the gas and water were metallically connected.
That would make them one line or two and each line must be bonded.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I have 2 apartments that need service upgrades. 100 amp each.

Each has its own meter for gas and water, we have to bond gas and water to the ground rod, here.

I know I can use 1 ground rod, but do I have to bond both gas and water for each apartment or just hit one? And were in the code book does it address this question.

The service wires tie in both from one drop.

Thanks for any input.


Try 250.104
 

Cavie

Senior Member
Location
SW Florida
I have 2 apartments that need service upgrades. 100 amp each.

Each has its own meter for gas and water, we have to bond gas and water to the ground rod, here.

I know I can use 1 ground rod, but do I have to bond both gas and water for each apartment or just hit one? And were in the code book does it address this question.

The service wires tie in both from one drop.

Thanks for any input.

Augie is correct. Also you need 1 EGC to 2 ground rods unless your prepared to prove 25 ohms on one.
 