Solar Power Installation

Status
Not open for further replies.

Agame

New member
Is it permissible to install cable tray from the roof of a building to the pas mounted 13.8 switchgear and run the proper cable free air to tap the line side of the LIPA?
 

rcwilson

Senior Member
Location
Redmond, WA
What's LIPA? Long Island Power Authority? I don't think it would be legal or smart to tap the line side of the switchgear and route unprotected 13.8 kV cables to the solar panel installation. Thsoe calbes would be service entrance cables.

The cables should be protected by a fused switch or circuit breaker in the pad mount switchgear.

Where is the transformer located that steps up the solar power inverter output to 13.8 kV? On the roof?
 