So for a transformer with Primary and Secondary OCPD, The primary OCPD is based upon the 125 % of the Primary Current with the option to go up to 250 % as permitted in the second half of of table 450.3(B) ? And if I increase OCPD must I then resize my primary conductors?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
what David said !
Keep in mind Art 450 deals only with the transformer and it's protection/installation. As noted in the FPNs at 450.3, Art 240 still covers the OCP for the conductors.
 