Mostly that a Yd0 configuration is impossible. The 0 would mean that the LV reference phasor (V_ab) is in phase with the HV reference phasor (V_AN). The only configurations possible with a "0" are Yy0, Dd0, or Dz0.What is the difference between the voltage ratio of a transformer with Yd0 and Yd1 configuration ?
Voltage ratio is the same when considering a 3? transformer as a unit.sorry for giving Yd0 , Its Ddo. and Yd1.
Don't know why you are getting those measurements. Can you provide more detail on the method and means of measurement?I have the following measurement ratio of a transformer with Yd1 configuration with primary voltage 34500 V
Tap Sec.Volts Ratio Vp/Vs
1 240.0 124.488 143.75
2 267.4 111.732 129
3 301.8 98.996 114
4 321.3 92.988 107
The measured ratio with instrument shows the values below "Ratio" whereas therotical values should be "Vp/Vs".
It could. Given a 30? vector and its polar coordinates as (ia,jb) and its magnitude as h, the ratios of the polar coordinate ia value to the vector magnitude are ia/h=cos30?=0.866.Well ,it really not an instrument dependent as it has been check with different measuring instrument.The methods uses injecting a known voltage on primary side and measures the secondry voltage.
I dont have exact calculation, but as the both side windings are of different configuration ,the factor root 3 is understandable. Does 30deg phase shift makes this difference?
Well that would be the problem. The primary-winding-to-secondary-winding voltage ratio should be, for a Yd1:I can see the formula used to calculate it . Vp/Vs X (root 3)/2.