NEC 517 Health Care Ground Fault/Coordination

Status
Not open for further replies.

btomallo

New member
517.17 requires two levels of ground fault protection. One on the main and a second on down stream feeders. My contention is that coordination with electronic trip CBs can achieve
more precise coordination than ground fault relaying. This meets the "or equivalent protective equipment" statement in the article.
Looking for some input. Thanks. :D

[ June 11, 2003, 02:53 PM: Message edited by: btomallo ]
 

bob

Senior Member
Location
Alabama
Re: NEC 517 Health Care Ground Fault/Coordination

517.17 give you the option of "other equivalent protective equipment". I agree with your statement regarding electronic trip CBs and I think they are at least equivalent to ground fault protection
 

roger deas

Member
Location
North_Carolina
Re: NEC 517 Health Care Ground Fault/Coordination

Would this meet the definition of "other equivalent protective equipment"? The problem is whether this down stream equipment can meet the definition of "Ground-Fault Protection of Equipment" per article 100 and required in 230.95.

Roger
 