Unbalanced current on neutral formula

Status
Not open for further replies.

bbuckway

Member
Can anyone help with how to figure what the unbalanced current would be on a Wye system neutral?
For example:
Phase A is 130 amps
Phase B is 110 amps
Phase C is 90 amps
What would the amps be on the neutral.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
There isn't really enough information to accurately determine the neutral current in your question. You need to know the phase angles of the 3 currents relative to each other.

The formula in the thread linked to by Derek would work if the phase angles of the 3 currents were 120 degrees apart.
 

Smart $

Esteemed Member
Location
Ohio
Can anyone help with how to figure what the unbalanced current would be on a Wye system neutral?
For example:
Phase A is 130 amps
Phase B is 110 amps
Phase C is 90 amps
What would the amps be on the neutral.
If you have Excel, download my calculator in the thread linked to earlier (let me know if the link does not work).

Anyway, your question leads me to ask if there is an ulterior purpose for asking? Mostly, are you using this to determine a size for a neutral conductor. If so, it's not how you determine the size.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
What's wrong with 120 degrees for 3 phase? What else do you have?

I'm not sure I understand your question. There's nothing wrong with 120 degrees for 3 phase. But you have what ever the load power factor gives you. Unless the power factor for each load is the same, you won't have 120 degree phase separation on the 3 line currents.
 