    What would a fast acting current limiting fuse be considered as? A time delay or non time delay for sizing purpose. We have a 4160 volt 250 hp motor - 33 FLA with 70 amp motor circuit current limiting fuses that blow on starting. Very expensive! The next size fuses are 100 amp. Is this acceptable to go to this size?
    #2
    I would test the motor before installing a larger fuse.
    Comment
      #3
      Motor is fine. This is not the only piece of equipment we have had this problem on. This plant has been mothballed for a few years and I've been told that someone was re-sizing just before they shut it down. I think that the fuses were larger size before. So possibly they are pulling a load on starting and this is the reason fuses are blowing. They don't blow every time either. I think it's just that we are bordering on the fuse limit and the next size is quite a bit larger.
      Comment
        #4
        Still wouldn't hurt to test the motor. I'm not a fuse expert by any means, but from my experience, a fast acting fuse is not a time delay fuse, if that helps any.
        [COLOR=navy]If you aim at nothing, you will hit it every time![/COLOR]
        Comment
          #5
          Current limiting and time delay are not mutually exclusive.
          Medium voltage fuses for motor applications, are not usually sized by continuous amps like 480V ones are.
          I have never heard of a 70A MV motor fuse, I would expect to see an 'R' rating instead.
          Just because you can, doesn't mean you should.
          Comment
            #6
            Or an "E"