Would a 480v transformered pilot light require fusing? I believe the lamp itself is 6 volts. If so what size?
Would a 480v transformered pilot light require fusing? I believe the lamp itself is 6 volts. If so what size?
As already stated, the light itself does not require fusing. Actually, it is in a sense a fuse itself (assuming incandescent).Would a 480v transformered pilot light require fusing? I believe the lamp itself is 6 volts. If so what size?
It's a self contained unit with transformer. 6.3 v bulb 150 ma with 380-480 primary. we are using it to just signal a circuit is energized. Would that be covered in the NEC ? If not we were thinking of fusing it to just protect the rather expensive pilot light. What fuse size would be appropriate? Not much load to speak of. thanks!
We had Allen Bradley 800T devices specified by several customers, and when the MCC was not equipped with a transformer or remotely powered, their 480:6.3 transformer lights were specified. I don't remember including them on any of our drawings ... we only did drawings when WE controlled the starters ... and looking back, the control circuit was probably locally fused with a small KTK type fuse (one? then, a pair today?)It's a self contained unit with transformer. 6.3 v bulb 150 ma with 380-480 primary. we are using it to just signal a circuit is energized. Would that be covered in the NEC ? If not we were thinking of fusing it to just protect the rather expensive pilot light. What fuse size would be appropriate? Not much load to speak of. thanks!
Not fusing it may present a problem if it actually falls under NEC pervue. Connecting to a circuit that has higher-rated ocp than the connecting wires makes those wires taps, and then subject to tap rules. So either install in a manner that is NEC compliant or install at a location and or manner that is not subject to NEC compliance.The MAJOR problem with that is that if you fuse it, and the fuse blows, you will THINK the power circuit is de-energized when it is not, exactly the OPPOSITE of what you want! It doesn't need to be fused in that circumstance, I would not do it.
...
Not so sure about this. I had this very discussion at length one time with a manufacturer's engineer. There is generally no requirement to protect any device with an OCPD. You do have to use them within their ratings. You do have to protect the conductors.You really have to study every device in the control circuit before selecting the fuse size.
Agreed on this one.Just FYI as you are doing that, look carefully at the VOLTAGE rating of any added pilot devices as well. A lot of things are only rated 300V max (i.e. NEMA A300 or B300) so you cannot use them at all on a 480V line voltage control system. This gets overlooked a lot lately because people are not used to 480V control circuits any more.