just want to check to see if I am correct.
Continuous Loads
4000 sqft @ 3va per ft 12000va
Show Window- 30ft @ 200va per ft 6000va
Sign 1200va
19200va X 1.25 = 24000va
Non-continuous Loads
76 receptacles @ 180va 13680va
First 10000va @ 100% 10000va
Remain 13680-10000=3680x50% 1840va
11840va
Air conditioner #1 6900va
Air conditioner #2 6900va
Cylinder Machine #1 1500va
Cylinder Machine #2 1500va
Compressor + 25% 2500va
Water Heater 3000va
Total Volt Amps 58140/240=242.25a
Panel @ 400a
Breaker @350a
Where can I cut the fat to keep it under 300A total?????
Please let me know if I missed a step or missed a reduction some where
:?