Breaker Sizing for motors with Soft Starters and VFD's

Status
Not open for further replies.

montericci

Member
Location
Ottawa, IL
Hi all.
I was wondering if there is a rule of thumb for sizing breakers that feed VFDs or Soft Starters that will in-turn operate motors.
I typically spec soft starts to ramp up and down and know that I can limit the current to 150% FLA.
With this in mind I've been specifying the breaker sizes at 150% of FLA or the next size up. I don't have to option to look up the Soft Starter or VFD recommendations as we have to simply state VFD or Soft Starter without being biased in the design. Please help if you can. Thanks
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
On VFDs you are required to have the feed conductors sized at a MINIMUM of 125% of the VFD's maximum rated amps, the motor is NOT factorerd into it. So if you have a VFD rated for 100HP but it is connected to a 50HP motor, you MUST size the conductors for the max amp rating of the VFD, not the motor. You can then use a smaller breaker if you so desire, but most people just size the breaker for the conductors.

On soft starters, all of the motor circuit breaker rules that apply in 430.52 do not change just because there is a soft starter involved. Conversely you should be able to use whatever breaker is listed for the motor HP as per usual, there is usually no need to up-size the breaker because if the starting current is going to be long and high enough to cause the breaker to trip, more than likely you will have exceeded the rating of the soft starter first. If you were to up-size the soft starter to compensate, then make the breaker match the soft starter size (assuming you don't end up violating a 430.52 rule in the process).
 
Last edited:
On VFDs you are required to have the feed conductors sized at a MINIMUM of 125% of the VFD's maximum rated amps, the motor is NOT factorerd into it. So if you have a VFD rated for 100HP but it is connected to a 50HP motor, you MUST size the conductors for the max amp rating of the VFD, not the motor. You can then use a smaller breaker if you so desire, but most people just size the breaker for the conductors.

Can you tell me where the code addresses OCPD and conductor sizing for circuits feeding VFD's?
I assume the conductors on the load side of the VFD is sized per 430.250?

Thanks,
James
 