    We are looking to connect a new water heater to an existing circuit. The existing circuit serves a 480/208 volt, 45 kva transformer. We placed a recording amp probe on the circuit breaker feeding the transformer and recieved A-24 amps, B-46 amps, C-26 amps. This transformer feeds three panels that serve a small cafe. I was suprised to see the high load on the B phase. Most of the loads are 120 volts (small coolers, sandwich presses, etc). Could this be an indication that the transformer is going bad or is this simply loads way out of ballance?
    #2
    I would guess the loads are simply out of balance. I would connect the water heater to the 2 lightly loaded legs.
    Our comedian shamelessly joked about a blackout. Talk about dark humor.
    Comment
      #3
      Unfortunately, the water heater is large at 24KW, 480 volt, 3 phase. It is possible that it is out of ballance, but I think it is unlikely with the type of loads connected. We are planning to measure the secondary voltages on the transformer. I suspect a problem with the transformer or improper grounding.
      Comment
        #4
        my money would be with mbrooke, unbalanced loads.
        At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
        Comment
          #5
          Ditto, unbalanced loads
          Comment
            #6
            May want to monitor the load over time, it may be balanced at times or unbalanced in a different way at times, depending on load usage patterns.
            I don't see how improper grounding will effect the current in the primary winding. It is going to draw whatever the load requires from it. If transformer is developing an insulation problem it likely will not last very long at all and you were just lucky to measure it at right time. If primary windings are a WYE configuration and neutral is connected to the common point this could be a problem, but will be a problem right away not some time later. Most transformers like you are describing are delta primary and this will not even be possible.
            I live for today, I'm just a day behind.
            Comment
              #7
              I agree it could be unbalanced load, but the 100% increase in the B phase looks strange to me. The readings are on the primary side of the transformer, which makes the amperage readings on the 208 volt side look even more strange. The transformer should only be serving a small cafe (about 900 square feet) that contains almost all 120 volt plug in equipment, with the exception of a residential range. The readings are the max readings over a 3 day period.
              Is it possible the transformer could have a bad coil? It is at least 30 years old and has been sitting in the back of a kitchen.
              Comment
                #8
                Can you get secondary current readings? If the secondary currents are unbalanced, can the cafe balance their single phase loads?
                Comment
                  #9
                  I am working on getting that. The transformer is tapped twice on the secondary and the secondary conductors are not as easily accessible as the primary conductors were.
                  Comment
                    #10
                    can you turn the water heater off and check the amperage readings again ?
                    Comment
                      #11
                      I don't follow your comment on the delta primary. If you have imbalances on your Wye secondary, this will translate into imbalances in your primary, regardless of connection.
                      Rob Wolf, PE
                      Comment
                        #12
                        The water heater is not connected yet. I am trying to determine if we have enough capacity in the circuit for the water heater. Capacity is difficult to find in this building.
                        Comment
                          #13
                          what size primary OCP is present for the transformer ? Is the transformer secondary protected at 125% ?
                          Comment
                            #14
                            The primary circuit breaker is 80 amps. The secondary has two taps. One uses a 125 amp, 3 pole enclosed circuit breaker and the other is in a main lug only panel that appears to be 225 amps, 3phase that then feeds a 100 amp, single phase load center. It is pretty old stuff and I know it is not up to current codes, but it may have been up to the code at the time of install.
                            Comment
                              #15
                              With the arrangement you describe with the two taps and single phase sub-panel, I would think you have an issue with unbalance.
                              But I'm not seeing the dilemma. You are hooking up a 24kW 480V 3ph load. I assume your not tapping the 480V transformer feeder; what is the 480V panel capacity and spare breaker availability?
                              Don't see how the transformer fits into it