Announcement
Collapse
No announcement yet.
Electrical load estimate for huge industrial facility
Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts
    Dear Electrical Designers,
    I need to estimate electrical load for a new industrial park of 30 Hectars with 1.5 M sq.ft food processing facility on it. This is a poultry processing facility with rendering plant and logistic center. Let's say 1M sq.ft is the processing plant, 0.3M - cold storage and 0.2 - all other facilities.
    I know this is not a simple task as there is very limited initial data, but i am sure many of you have experience with industrial facilities and can help at least with W/sq.ft. It is initial estimation, we do not need to be precise.
    Also, there is a site and the site will mainly be a huge parking lot. What is w/sf.ft for parking lot lighting?
    Thank you in advance for your help!
    #2
    How much of the heating (both climate and process) is going to be electric? Well that would be my first question.
    Proverbs 31;10
    Comment
      #3
      All cooling will be electric and very little heating will be electric: (5-10%) of total heating.
      Comment
        #4
        To answer your question, you need to know and assign the power consumption per square foot for the different building types.
        Based on recent experience, an allowance of 20W/SF should get you started in the right direction.
        Check the IEEE Red Book, and the refrigeration contractor on the project, for a more accurate answer.
        Comment
          #5
          For the parking lot, a good reference would be the Illumination Engineering Society - North America (IES-NA).
          They will likley suggest a range of foot candles illumination ranging from 1/2fc to 1fc in the parking area, up to 5fc at the intersections.
          I would typically allow 1/2W/SF of parking, LED will be much lower IF the budget allows.