How do you calculate the current from a 75 hp motor, 3 phase, 460 Volt?
T tmag28 Member Location oxnard,ca Nov 29, 2012 #1 How do you calculate the current from a 75 hp motor, 3 phase, 460 Volt?
bob Senior Member Location Alabama Nov 29, 2012 #2 no need. check here http://www.electricmotorshop.net/index.php?option=com_content&view=article&id=687&Itemid=352
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 29, 2012 #3 If you need the current for anything to do with the rules in the NEC, you must use the currents shown in Tables 430.247 through 430.251. In your case it is Table 430.250 and the current is 96 amps.