RJRUBLE
Member
- Location
- Southern California
- Occupation
- Electrical Contractor
In 210.52 it fully explains about Receptacle requirements in a kitchen. My question is that the builder I work for wants to replace 1 of the DUPLEX receptacles with a the new Leviton T5630-W Combination Device. If not familiar it is a single 3 prong receptacle and 2 USB outlets. So you would loose 1 actual receptacle. Does the code specify if a receptacle in a kitchen needs to be a duplex or will this combo device suffice. I am concerned that a homeowner may miss and want the additional spot to plug something in. Any thoughts?