We have a project with a tight vertical fit. Our primary feeds running to a transformer will have to run through the bottom of the enclosure of the secondary OCPD of said transformer. NEC 200.6(D), 210.4(D), and 300.4(C)(1) seem to indicate this is ok. Anyone else run into this?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since you said switchboard this may apply:

408.3 Support and Arrangement of Busbars and Con-
ductors.
(A) Conductors and Busbars on a Switchboard or Pan-
elboard. Conductors and busbars on a switchboard or pan-
elboard shall comply with 408.3(A)(1), (A)(2), and (A)(3)
as applicable.
(3) Same Vertical Section. Other than the required inter-
connections and control wiring, only those conductors that
are intended for termination in a vertical section of a
switchboard shall be located in that section.
Exception: Conductors shall be permitted to travel hori-
zontally through vertical sections of switchboards where
such conductors are isolated from busbars by a barrier.
 