Gentlemen?
In my experience there are two predominant Phasing-In problems associated with a Tie-Breaker: a) Reversed Phase?Sequence (RPS); and b) Different-Winding Polarity, (DWP)!
The first problem, RPS, can be corrected with the Phase-Rollover technique. The problem occurs when the phase-sequence of, say the left-hand supply to the breaker is A-B-C, while the right-hand supply is C-B-A!
It is usually occurs because of an electrical-design flaw, that is, the bus or feeder-cable between the Xfmr and Switchgear, is drawn as a ?mirrored? arrangement (ABC-CBA) rather than an identical Arrangement (ABC-ABC)! (Remember, in trig it was called ?reflection about the vertical-axis?!)
As an example, consider a Wye, 120 V system. Then the ?measured paired? voltages are: A-A? = 0 Volts; B-B? and C-C? = sqrt(3) x Nominal or 208 Volts!
The second problem, DWP, can?t be solved using the Phase-Rollover technique, because it involves changes to the Xfmr?s internal connections! It usually occurs when one or the other Xfmr is replaced!
The corresponding ?measured pairs? are: A-A?, = 2 x nominal or 240 Volts; B-B? & C-C? = Sqrt(3) x Nominal or 208 Volts!
Regards, Phil Corso