    I have conduits that run from interior boxes out to exterior light fixtures. The exterior boxes are filling with water from condensation. Should I seal the seal tight conduit with silicon caulk or is special electrical caulking required?

    #2
    If it is condensation duct seal should do it.

    Besides the NEC requires sealing conduits in some applications.

    300.7 Raceways Exposed to Different Temperatures.
    (A) Sealing.
    Where portions of a raceway or sleeve are
    known to be subjected to different temperatures, and where
    condensation is known to be a problem, as in cold storage
    areas of buildings or where passing from the interior to the
    exterior of a building, the raceway or sleeve shall be filled
    with an approved material to prevent the circulation of
    warm air to a colder section of the raceway or sleeve. An
    explosionproof seal shall not be required for this purpose.

    Comment


      #3
      Originally posted by mlnk View Post
      I have conduits that run from interior boxes out to exterior light fixtures. The exterior boxes are filling with water from condensation. Should I seal the seal tight conduit with silicon caulk or is special electrical caulking required?
      You might want to also consider some kind of drain.
      Bob

      Comment


        #4
        Originally posted by mlnk View Post
        I have conduits that run from interior boxes out to exterior light fixtures. The exterior boxes are filling with water from condensation. Should I seal the seal tight conduit with silicon caulk or is special electrical caulking required?
        BTW, it is silicone caulk, not silicon caulk. Silicone is to silicon, as polyethylene is to carbon.