    Hello to all first off. I am a commercial electrician and recently landed a job doing more industrial than commercial. Anyway, I do not understand three phase 240v... I get the wild leg B phase is high leg but I don't get how A to ground reads 120v, B - G reads 240volts, and C to ground is 120v. Its almost like single phase 240??...????????. How does a a 2 pole breaker get 240v when B phase is 240v?? Or a motor say wye example, 3 phase in peckerhead would be L1-a, L2-b, L3-c, 4-7, 5-8, 6-9.. How do I run 240v 3phase to motor??? Hope that isn't to confusing. I just can't wrap my head around this Delta. Thanks
    #2
    Here's an illustration that should help.
    Roger
    Comment
      #3
      For the motor hook-up you look at the motor nameplate and make the hook-up based on the supply voltage.
      Don, Illinois
      (All code citations are 2017 unless otherwise noted)
      Comment
        #4
        When it's 240V you use your low voltage L1 is 1,7, L2 2,8, L3, 3,9 and 4,5,6 tie together.
        If Billy Idol is on your playlist go reevaluate your life.
        Comment
          #5
          thanks
          But wouldn't that be single phase?? @roger, lets say I am landing a standard 2 pole breaker. Would AB = 240v on a delta 3 phase, or BC? Is it possible to run 240v just from B. (theoretically speaking). If B to ground is 240, why do I need A or C?? Or if I landed a single pole on B, would it get 240 or 120v? I'm use to 120/208, 277/480.. Thanks to all
          Comment
            #6
            That assumes that that motor is a wye connected motor. We don't know that.
            Don, Illinois
            Comment
              #7
              He said wye in the OP.
              Comment
                #8
                B to ground should be 208V. Many places just use the A and C phases with ground as 240V split (single) phase for most of the loads.
                Comment
                  #9
                  No. It's three phase...... L1, L2, L3..... A, B, C. A to B 240V, B to C 240V, C to A 240V.
                  Comment
                    #10
                    Adave
                    Not 208. A-g= 120, B-g= 240, c-g=120
                    @aDave, thank u sir, that registered. So, regardless of B @ 240v any order of the phases still gets me at 240v, correct? Obviously not considering rotation, I know to switch out a phase/rotate..
                    Comment
                      #11
                      Not 208. A-g= 120, B-g= 240, c-g=120v
                      Are you testing with a digital meter or a wiggy?
                      Comment
                        #12
                        That is not clear to me, because the word "example" was used along with wye.
                        Don, Illinois
                        Comment
                          #13
                          wiggy!!
                          No! Digi multimeter..
                          @Don , as In not center tapped delta. Like 277/480 ABC-G= 277, AB=480, BC=480V
                          Comment
                            #14
                            Yes. Phase to phase is 240V every time.
                            Got to run for now. The fact this is driving you crazy means you can get this. Hang in there.
                            Comment
                              #15
                              dave
                              Really?? Billy idol hater?? Lol, rock the cradle, white wedding.. Classic!