I just did a service and per N.E.C. the high leg goes to c phase on the meter. So does that mean I change the high leg in the M.D.P also or leave it.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Welcome to the forum.

I'm not 100% sure what you are working on but I do know that it is common for the utility to land the high leg from a delta system on C phase and for us electricians to roll it over to B phase....that was not always required.....existing systems are allowed to keep phases the same as they always were.
 

electricalist

Senior Member
Location
dallas tx
Here the meter enclosure states hi leg to be on c phase,then we roll it to B phase like Mr. Dave,be carefull if theres multiple disconnects after the meter and if there are parallel runs.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
One minor clarification which is probably a matter of semantics (unless you are using 208 equipment). If you have a "high-leg" (208 volt to ground), you have a 240/120 three phase delta system with 240 phase to phase.
You most likely already know that and I don't want to be insulting.
Your header "120 208 with high leg could be a bit deceiving to those accustomed to a 208/120 wye system which has no high leg.
 