Beast of Burden. Also a high current version called Mega-Beast. Basically a hair dryer type heating/fan unit that loads the service. Four wires...two hot, one neutral, one ground for safety. There are two voltmeters to measure line to neutral voltage under load on each leg. You switch the load (line to neutral) from one phase to the other. If the voltages drop the same for each leg, you have line drop, usually due to a long secondary. If the voltage drops when one leg but not the other, you have a problem on that leg. If the voltage drops on the loaded leg and rises on the opposite leg, you have a neutral problem. Sounds confusing, but simple and easy to use. Beast loads at 30A. Mega-Beast loads at up to 80A. Pretty spendy, though. Probably used ones on Flea-Bay. The utility doesn't usually do resistive testing because that would require a trip to the transformers.
It also can plug into the meter socket, but the utility would probably be unhappy with you pulling their meter.