Grounding Requirments History

Status
Not open for further replies.
We perform inspections on existing and older facilities and find where the equipment bonding conductor is undersized by one size. Did the code change at some point and increase the wire size on grounding and bonding? If so when?
thanks,
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
We perform inspections on existing and older facilities and find where the equipment bonding conductor is undersized by one size. Did the code change at some point and increase the wire size on grounding and bonding? If so when?
thanks,

What equipment bonding conductor are you asking about? There is not just 1. All of them are sized according to table 250.122.

The system or main bonding jumper is a different animal.
 
Status
Not open for further replies.
Top