tandem breakers and panel design

Status
Not open for further replies.

mikewillnot

Member
Location
Rochester, NY
Occupation
electrical contractor
New-ish Square D QO 30-space panel, need 2 more spaces.
Tandem breakers come in two types, as pictured below, courtesy 480Sparky.
Mechanically, I could install the lower type in any QO panel, and it would fit. It wouldn't be "correct" though. WHY? (And I don't just mean, "because they said so.") What's wrong, electrically, with putting one of these in a 30-space (in contrast to a 30/40-space) panel? I.e., what's different about the two panel designs, and what's different about the two tandem types, besides the hook/slot?

I'm reading that it's somehow related to current limiting, to CTL vs non-CTL breakers. (I don't quite get that either, though I understand the basic concept of CTL.) IF the difference between tandems is CTL/non-CTL, which is which, and what's the logic behind CTL tandems or non-CTL tandems being OK in some cases vs. other cases, or some panels vs other panels?

wol_error.gif

qo_tandems.JPG


I read every thread I could find, and they don't help me explain the issue to homeowners, short of just saying "because it's not allowed."

For reference purposes (and complicating matters only slightly) newer breakers (side-by-side) look like this:

wol_error.gif
Click this bar to view the full image.
QO_tandem3.JPG
 

growler

Senior Member
Location
Atlanta,GA
I think the keyword is "listed".

It cost manufacturers lots of money to get a product tested and UL approved.


It's not allowed may not be good enough for a homeowner but it's good enough for me. If a product is approved then it's not my responsibility, it's already tested for a certain use. If I choose to do something like modify a product or use it in a way that's not approved then it is my responsibility.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I think when it comes to residential plug on type panels it is all about marketing.
 

JRW 70

Senior Member
Location
Eastern Central Missouri
Occupation
Testing and Engineer
I know it comes back to listing, but what is the difference
between a tandem 20 amp (possibly drawing up to forty
amps on one clip) and a two pole 40 amp or up in the same
clip space. It seems to be policy overriding basic electrical
principles, since the bus that these clip to can handle well
over the tandem C.B. The only thing I could think of at this
moment is heat transfer issues.

JR
 

iwire

Moderator
Staff member
Location
Massachusetts
I think the keyword is "listed".

It cost manufacturers lots of money to get a product tested and UL approved.


It's not allowed may not be good enough for a homeowner but it's good enough for me. If a product is approved then it's not my responsibility, it's already tested for a certain use. If I choose to do something like modify a product or use it in a way that's not approved then it is my responsibility.

I agree with this 100%.

If we were to look in my own homes electrical panel we would find many different brand breakers in my Murry panel.

On the other hand I would never do that with a customers panel.
 

iwire

Moderator
Staff member
Location
Massachusetts
I know it comes back to listing, but what is the difference
between a tandem 20 amp (possibly drawing up to forty
amps on one clip) and a two pole 40 amp or up in the same
clip space. It seems to be policy overriding basic electrical
principles, since the bus that these clip to can handle well
over the tandem C.B. The only thing I could think of at this
moment is heat transfer issues.

JR

There is nothing different other than the listing. Nothing.

Acept it is just a matter of what the manufacturer chose to have it listed for.

It is not overriding any electrical principles because it is not about electrical principles. It is about making money.
 

kwired

Electron manager
Location
NE Nebraska
I know it comes back to listing, but what is the difference
between a tandem 20 amp (possibly drawing up to forty
amps on one clip) and a two pole 40 amp or up in the same
clip space. It seems to be policy overriding basic electrical
principles, since the bus that these clip to can handle well
over the tandem C.B. The only thing I could think of at this
moment is heat transfer issues.

JR
Forty amps on one clip is not the issue - that bus is rated for up to 125 amps in most panels. The difference is the breaker without the rejection feature is not a CTL rated breaker and the one with the rejection feature is CTL rated. Not saying they may not be the same thing internally, but the listing still is non CTL if it doesn't have the rejection feature.

ETA

You don't find this issue with the Homeline series because it was not around yet before they required CTL rated breakers, so all the Homeline tandems have the rejection feature and are CTL rated as there is no existing panels old enough that non CTL is an issue with them.
 
Last edited:

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Loadcenter style panelboards have always had limitations on the use of tandem breakers. UL required panels be supplied with wiring diagrams showing how many tandems were allowed in the panel and which breaker positions could accommodate them. But people, including electricians, kept installing tandems wherever they wanted.

So, roughly 50 years ago UL and the NEC came up with the concept of breakers and panels with circuit limiting (CTL) construction. But, because breaker panels had been in existence for several decades, an exception for 'existing installation' was included. CTL usually involved some type of rejection clip, the rest of the breaker remained the same, as it was not cost effective to have two 'lower volume' breaker mechanisms.

There are inspectors that do not approve the non-CTL breaker in panels boards installed after 1965.
When I entered the trade in the early 70's, non-CTLs breaker were called 'cheaters'.
But, to this day it seems many electrical wholesalers probably still sell more non-CTL than they do CTL breakers (many manufacturers sell only CTL breakers to home centers).
 

JRW 70

Senior Member
Location
Eastern Central Missouri
Occupation
Testing and Engineer
When I wired panels, the specs. disallowed the use
of tandem breakers, ( on many of our projects )
so we ended up with more panelboards/breakers and a
happy design Engineer. He felt that there were too many
small components in the tandems, so they were never really
an option. They wanted full size breakers for basically
everything ( with the exception of fuses, where appropriate )

I definately agree this is a money maker for manufacturers
and "overly" cautious Engineers that I have dealt with.

JR
 
Last edited:
Loadcenter style panelboards have always had limitations on the use of tandem breakers. UL required panels be supplied with wiring diagrams showing how many tandems were allowed in the panel and which breaker positions could accommodate them. But people, including electricians, kept installing tandems wherever they wanted.

So, roughly 50 years ago UL and the NEC came up with the concept of breakers and panels with circuit limiting (CTL) construction. But, because breaker panels had been in existence for several decades, an exception for 'existing installation' was included. CTL usually involved some type of rejection clip, the rest of the breaker remained the same, as it was not cost effective to have two 'lower volume' breaker mechanisms.

There are inspectors that do not approve the non-CTL breaker in panels boards installed after 1965.
When I entered the trade in the early 70's, non-CTLs breaker were called 'cheaters'.
But, to this day it seems many electrical wholesalers probably still sell more non-CTL than they do CTL breakers (many manufacturers sell only CTL breakers to home centers).

Jim, do you know why exactly they felt the need to limit the number of tandems or circuits? Was it some sort of formula for number of circuits per physical size That you couldnt exceed?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Jim, do you know why exactly they felt the need to limit the number of tandems or circuits? Was it some sort of formula for number of circuits per physical size That you couldnt exceed?
I seem to recall discussion about this coming from the New York area, kind of like the original 42 circuit limitation. But as I said they have had limits on tandems for at least 60 years.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I wonder if there ever was a real technical reason for limiting the use of tandems? If you have a panel with a 125 amp bus and limited to 30 breakers, what physical change would be made when they had 30/40 panel with a 125 amp bus? I bet none.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I wonder if there ever was a real technical reason for limiting the use of tandems? If you have a panel with a 125 amp bus and limited to 30 breakers, what physical change would be made when they had 30/40 panel with a 125 amp bus? I bet none.
Well, it is a little simplistic, but the biggest physical change is probably the inclusion of rejection tabs in some of the positions. :angel:
I doubt that the bus is any different.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I wonder if there ever was a real technical reason for limiting the use of tandems? If you have a panel with a 125 amp bus and limited to 30 breakers, what physical change would be made when they had 30/40 panel with a 125 amp bus? I bet none.
My guess is that this was a 'trade based' decision to encourage the replacement of equipment and its associated labor skills.
 