Extending Short Neutral Wire

Status
Not open for further replies.
Hi,

I have what I think is a simple question: I am replacing an existing breaker in the panelboard with a new GFCI/AFCI breaker which of course requires the neutral to be wired to it. The problem is that the existing circuit neutral is too short to reach the breaker so I need to splice the neutral (wire nut) so it can reach the breaker.

My question is, does the code allow this? I looked at 312.8 and my reading of it says that this is allowed.

Thanks
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Hi,

I have what I think is a simple question: I am replacing an existing breaker in the panelboard with a new GFCI/AFCI breaker which of course requires the neutral to be wired to it. The problem is that the existing circuit neutral is too short to reach the breaker so I need to splice the neutral (wire nut) so it can reach the breaker.

My question is, does the code allow this? I looked at 312.8 and my reading of it says that this is allowed.

Thanks

It is allowed. You are correct.
 

kwired

Electron manager
Location
NE Nebraska
that's not entirely true, you can't splice a wire passing through a panel you can only splice a wire that terminates in the panel. But that condition shouldn't arise as a wire cant pass through a panel anyway.
You want to clarify that some more? I don't see that being true as a general rule, otherwise maybe some specific condition doesn't allow passing a conductor through a panelboard? Splices are not a problem, they just need be accessible other then direct buried conductors - but those need a splicing method that is intended for direct burial.
 

iwire

Moderator
Staff member
Location
Massachusetts
you can't splice a wire passing through a panel you can only splice a wire that terminates in the panel.

There is nothing in the NEC that says that. It may be a local rule for you.

a wire cant pass through a panel anyway.

The NEC allows that as well.

Keep in mind that to the NEC a 'Panel' is a 'panelboard' which is covered in article 408 and a it is just the bus bars and breakers without an enclosure.

Panels are installed in cabinets covered in article 312.

The rules for splicing in cabinets are found in 312.8.

Here are a couple of helpful NEC definitions.


Panelboard. A single panel or group of panel units designed
for assembly in the form of a single panel, including
buses and automatic overcurrent devices, and equipped
with or without switches for the control of light, heat, or
power circuits; designed to be placed in a cabinet or cutout
box placed
in or against a wall, partition, or other support;
and accessible only from the front.

Cabinet. An enclosure that is designed for either surface
mounting or flush mounting and is provided with a frame,
mat, or trim in which a swinging door or doors are or can
be hung.
 

kwired

Electron manager
Location
NE Nebraska
There is nothing in the NEC that says that. It may be a local rule for you.



The NEC allows that as well.

Keep in mind that to the NEC a 'Panel' is a 'panelboard' which is covered in article 408 and a it is just the bus bars and breakers without an enclosure.

Panels are installed in cabinets covered in article 312.

The rules for splicing in cabinets are found in 312.8.

Here are a couple of helpful NEC definitions.
I agree with what you said, and I guess maybe his words were right, you can't splice in a panelboard, but you can splice in the cabinet that contains the panelboard, but am guessing that was not what his intended meaning was.:)
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
that's not entirely true, you can't splice a wire passing through a panel you can only splice a wire that terminates in the panel. But that condition shouldn't arise as a wire cant pass through a panel anyway.

If you cut a wire passing through, and then jumper the two wires back together again with a pair of wire nuts, have you not created a couple terminations within the panel?

Oh dear, I've just gone cross-eyed.
 

kwired

Electron manager
Location
NE Nebraska
If you cut a wire passing through, and then jumper the two wires back together again with a pair of wire nuts, have you not created a couple terminations within the panel?

Oh dear, I've just gone cross-eyed.
But he says there won't be a wire passing through the panel to possibly cut in the first place.
 