Supply Conducters

Status
Not open for further replies.

sabar

Member
This is for an installation with a disconnect that requires copper supply conductor, On line side of disconnect can you use aluminum & load side use copper to satisfy the copper supply conductors for termination in unit
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Not sure I understand your question.

If the disconnect requires CU conductors only then that is what you have to use for line and load.

A more common situation is the equipment being fed from a disconnect. requires CU conductors. In that case you could feed the disconnect with AL and go out of it with CU provided the lugs are listed for both metals.
 

kwired

Electron manager
Location
NE Nebraska
A more common situation is the equipment being fed from a disconnect. requires CU conductors. In that case you could feed the disconnect with AL and go out of it with CU provided the lugs are listed for both metals.

Me thinks that is what he was trying to ask if he can do.:D
 

sabar

Member
HVAC supply conducters

HVAC supply conducters

Yes , that was my inquiry just wanted to bounce it around. Feed disconnect with AL, unite requires supply conductors to be Cu. so supply unit with Cu

Thank you for your replies
 