This job is stretching my experience so I need some sanity checking. Important customer to me so I want to get it right. 480/277 3 phase Y.
This outside installation is spread over concrete wall of this old very large 200 ft high bldg.
The outside Switchboard will have outdoor conduit runs to 4 x 200A and 1 x 400A main breaker panels. Ground and neut will not be bonded in these.
The service disconnects will be in the Switchboard and will be moulded case cct breakers (4 x 200A; 1 x 400A).
This is a flat roof Switchboard. It will be mounted to the wall. Grd and neut will be bonded in this enclosure at point of service.
Q1:
Is it per code to exit these feeder conduits through the roof of Switchboard enclosure????
Neutrals will be same of gauge as current carrying conductor in all cases (just to be on safe side).
Do these following selections for sizing look good??. I always want to control the cost yet keep the installation not too stressful on moi or on the products.
Q2:
The 1000 kVA XFR secondary is connected to incoming side of Switchboard using 4 parallel feeds of 300A each. For each run will use:
The runs for the 200A panels will be:
The run for the 400A panel will be:
I am so impressed with the sheer professionalism of this superb website. I hope to give back in the future.
This outside installation is spread over concrete wall of this old very large 200 ft high bldg.
The outside Switchboard will have outdoor conduit runs to 4 x 200A and 1 x 400A main breaker panels. Ground and neut will not be bonded in these.
The service disconnects will be in the Switchboard and will be moulded case cct breakers (4 x 200A; 1 x 400A).
This is a flat roof Switchboard. It will be mounted to the wall. Grd and neut will be bonded in this enclosure at point of service.
Q1:
Is it per code to exit these feeder conduits through the roof of Switchboard enclosure????
Neutrals will be same of gauge as current carrying conductor in all cases (just to be on safe side).
Do these following selections for sizing look good??. I always want to control the cost yet keep the installation not too stressful on moi or on the products.
Q2:
The 1000 kVA XFR secondary is connected to incoming side of Switchboard using 4 parallel feeds of 300A each. For each run will use:
3" plastic conduit
500 MCM XHHW Al
3 wires in cable
Neutral
Ground #2 Al
Q3:
The runs for the 200A panels will be:
480/277 V 3 ph 200 A
300 MCM XHHW Al
3 wires in cable
Neutral
Grd #4 Al
3” plastic conduit
Q4:
The run for the 400A panel will be:
480/277 V 3 ph 400 A
700 kcmil XHHW Al
3 wires in cable
Neutral
Neutral
Grd #1 Al
4” plastic conduit