Looking for a 400A electrical service panel with 350A main circuit breaker option.

Status
Not open for further replies.

WillJenn71

New member
Does anyone know where I can get a 400A main service panel with the option of installing a 350A main breaker? It seems that all I can find are 400A panels with maximum of 200A main breakers.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Are you looking at 400 amp meter mains? Those units usually only allow 2-200 amp breakers. You may have to go to a mdp to install a 350 amp breaker on a buss bar.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Does anyone know where I can get a 400A main service panel with the option of installing a 350A main breaker? It seems that all I can find are 400A panels with maximum of 200A main breakers.

can you get a 400 amp frame with a 350 amp trip unit?
I think square D may have such an animal.
 
Status
Not open for further replies.
Top