Background:
A client was using 2 portable generators in the past; a Generac 5KW and a Yamaha 2.4 KW Inverter for their home office. They were not operating in parallel, they were used using separate cables feeding the appliances, lights, while the inverter was eeding the home office UPS's which were connected to their pc's, router, cable box/modem, FIOS Phone/Internet. Everything was working fine.
They decided to go with a 30 AMP interlock system using the 5 KW generator, which I installed and tested out.
During testing, their UPS's would trigger, as was expected, during appliance power surges, and even during printer active job surges.
------------------------------------------------------------------------------------------------------------
The question is, can they also use their inverter to power their home office:
The home office has a completely isolated (from house power) electrical feed cable, which was used originally when they were using the 2 generators.
All they want to do is connect the inverter to their 5 UPS's. These UPS's power 3 computers, cable modem/gigabit sw, FIOS modem/gigabit sw, and one printer which is connected to the surge protector side.
Initially everything seemed fine to me, and even the inspector did not have an issue when I asked.
But as I thought about it more,
They have another 3 cable modems in the house, which will be powered by the other generator. They also have other computers in the house, using CAT5 cables, which will be powered by the inverter generator.
SO here is the BIG Question:
Can we do this? Is there a code covering this:
even though the electrical circuits are completely isolated, there are secondary connections through the RF/video/CAT5 conenctions.
BTW: The cable and FIOS are grounded to the house water pipe, as is the main power. The 5 KW generator is left bonded; it is not grounded using additional means.
A client was using 2 portable generators in the past; a Generac 5KW and a Yamaha 2.4 KW Inverter for their home office. They were not operating in parallel, they were used using separate cables feeding the appliances, lights, while the inverter was eeding the home office UPS's which were connected to their pc's, router, cable box/modem, FIOS Phone/Internet. Everything was working fine.
They decided to go with a 30 AMP interlock system using the 5 KW generator, which I installed and tested out.
During testing, their UPS's would trigger, as was expected, during appliance power surges, and even during printer active job surges.
------------------------------------------------------------------------------------------------------------
The question is, can they also use their inverter to power their home office:
The home office has a completely isolated (from house power) electrical feed cable, which was used originally when they were using the 2 generators.
All they want to do is connect the inverter to their 5 UPS's. These UPS's power 3 computers, cable modem/gigabit sw, FIOS modem/gigabit sw, and one printer which is connected to the surge protector side.
Initially everything seemed fine to me, and even the inspector did not have an issue when I asked.
But as I thought about it more,
They have another 3 cable modems in the house, which will be powered by the other generator. They also have other computers in the house, using CAT5 cables, which will be powered by the inverter generator.
SO here is the BIG Question:
Can we do this? Is there a code covering this:
even though the electrical circuits are completely isolated, there are secondary connections through the RF/video/CAT5 conenctions.
BTW: The cable and FIOS are grounded to the house water pipe, as is the main power. The 5 KW generator is left bonded; it is not grounded using additional means.