Cannonmn

Member
Location
Northern va
Here's the label with diagrams:


img_0870.jpg
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
This is a delta to delta to wye step down.
If you use it for step up you will end up with either ungrounded or corner grounded delta. Is that OK?

Sent from my XT1585 using Tapatalk
 

Cannonmn

Member
Location
Northern va
Will this transformer work ok when reverse-fed to get 480/3?

Will this transformer work ok when reverse-fed to get 480/3?

Data in pic below. I need to create 480v.3phase to run machine tools. I have a qualified electrician ready to hook up transformer but he's not a transformer expert so I want to find out about issues in doing this. I know influx current will be momentarily high and we're prepared to deal with that. Big question I tried to get GE customer service to answer was whether this transformer, given where taps are etc., will present any huge problems. The GE instruction cited on the label pictured, only mentions the high influx current issue, but nowhere says you cant reverse-feed it. Then there's the ground issue. The only way I've read that you can create a ground for your loads is to use a corner ground, typically done by grounding the B phase. Comments?
img_0007-e1499646445958.jpg
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The only simple grounding solution for a delta is the corner ground.
Motors should have no problems with it, but some VFDs or built-in speed controls will not like it and at a minimum may need modification.

Sent from my XT1585 using Tapatalk
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Data in pic below. I need to create 480v.3phase to run machine tools. I have a qualified electrician ready to hook up transformer but he's not a transformer expert so I want to find out about issues in doing this. I know influx current will be momentarily high and we're prepared to deal with that. Big question I tried to get GE customer service to answer was whether this transformer, given where taps are etc., will present any huge problems. The GE instruction cited on the label pictured, only mentions the high influx current issue, but nowhere says you cant reverse-feed it. Then there's the ground issue. The only way I've read that you can create a ground for your loads is to use a corner ground, typically done by grounding the B phase. Comments?
The short answer is yes, this transformer can be fed from either side. Back in the old days, like before 2011, it was done all the time, backfeed a transformer, corner ground it and your done.

Electrons are dumb as a rock and don't care about labels or tech support opinions. Motors are dumb as a rock, they don't care about anything other than having the correct voltage fed to them. Electronics are a different matter, they are still dumb, but they require some special handling.
 

JFletcher

Senior Member
Location
Williamsburg, VA
If you need a wye secondary (277/480V; i.e., a neutral), then that transformer will not work. It is also 480V - 208Y/120V, so if reverse fed, you need 208V on the primary; 240V will be too hot (high a voltage). Yes, it can be fed from either side.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer

What's interestingly relevant in that paper is the fact that it indirectly states that for GE, they are insisting that step-up transformers be custom built to order, which then plays to the NEC requirement* that transformers used to step-up voltage be approved for use by the manufacturer, either on the nameplate of in some other form of documentation. That paper to my reading means you cannot legally use GE transformers for step-up.

*Depending on which code cycle you are on.
 