I am in the middle of a project that consists of steel stud framing using all MC / conduit methods and now have a hiccup.
The friendly inspector informed me that we have been incorrectly using firestop (3M CP25WB+) to seal our penetrations through the steel top plate. He is of course correct in this observation, my question is do you all know of any firestop / draftstop (different areas) product that I could use to seal a 3/4" - 1" hole containing MC cable.
I am trying not to resort to pulling cables out and placing sheetrock in the cavities, securing sheetrock, drilling holes, replacing cables and then applying firestop. I have been told there is a Hilti product that I could potentially use, but you have to be Hilti certified to apply it...
And yes, now that I have done further research I see now it was a bonehead move. Not that it matters, but we have done it for years and every other inspector has been wrong in approving it.
The friendly inspector informed me that we have been incorrectly using firestop (3M CP25WB+) to seal our penetrations through the steel top plate. He is of course correct in this observation, my question is do you all know of any firestop / draftstop (different areas) product that I could use to seal a 3/4" - 1" hole containing MC cable.
I am trying not to resort to pulling cables out and placing sheetrock in the cavities, securing sheetrock, drilling holes, replacing cables and then applying firestop. I have been told there is a Hilti product that I could potentially use, but you have to be Hilti certified to apply it...
And yes, now that I have done further research I see now it was a bonehead move. Not that it matters, but we have done it for years and every other inspector has been wrong in approving it.